Old 10th October 2008, 4:18 PM   #16
Squeezer
Member
 
Squeezer's Avatar
 
Join Date: Feb 2002
Location: Adelaide
Posts: 6,425
Default

One of our workgroups were conducting a training session and they grabbed a crusty old Switch as there were approx 15 people with PCs laptops int he training session. Someone managed to put a cat5 cable from one port of the switch straight into another port on the switch.

Causes a few problems as the switch further up the rung wasnt configured to stop broadcast storms
Squeezer is offline   Reply With Quote

Join OCAU to remove this ad!
Old 11th October 2008, 7:19 AM   #17
The_Derro
Member
 
Join Date: Jul 2001
Location: Chatswood, Sydney.
Posts: 518
Default

Quote:
Originally Posted by Iceman View Post
They were.. briefly.

"Why can't I copy files while he's copying files" "Why do I keep getting thrown out of MSN"

That one was a tricky one to track down. It sounds simple once you know the answer but who compares MAC addresses to check for duplication? It wasn't like they were all 00's or FF's..
Yep, been there, done that We had 5 PC's.. all on the same switch, all with the same MAC address. It presented in odd ways too, but wasn't consistent - a case of one user saying "Hey, I just lost access"..

It was only when I was trying to do a copy on all 5 at once and noticed that only a single PC would work at once.. check ipconfig on all and sure enough.. same MAC address on each one. Back to the wholesaler they went!
The_Derro is offline   Reply With Quote
Old 11th October 2008, 11:30 AM   #18
tensop
Member
 
Join Date: Mar 2002
Posts: 1,131
Default

Previous network admin saved the AD DNS zonefile, inserted some odd invisible(to dnsmgmt atleast) characters, then re-loaded it back into dns+active directory on his last day.
tensop is offline   Reply With Quote
Old 11th October 2008, 6:49 PM   #19
checkers
Member
 
checkers's Avatar
 
Join Date: Jan 2007
Location: Perth
Posts: 613
Default

Just discovered that the NIC that comes with Dell Vostro desktops (intel onboard something-or-other) breaks vmware. With a FreeBSD VM, I kept on getting errors that received packets were 4 bytes larger than the max allowed MTU... no matter what the MTU was set to on the host & in guest!

This confused me for a few days while I tested across ubuntu 64 and windows hosts and saw it fails, then moved to other identical machines (which since they are dells had other random NIC brands) to see it work fine.
__________________
CCCP
checkers is offline   Reply With Quote
Old 11th October 2008, 11:11 PM   #20
fR33z3
Member
 
Join Date: Jul 2001
Location: Perth
Posts: 2,092
Default

oh...i bought a carton for this cockup in my younger days...

Take work laptop home, need to copy files from PC to xbox, but can't be arsed moving it closer to the PC, so connect xbox to laptop, and bridge wired + wireless connections. Brilliant. Works a treat.

Get back into work. Plug in. Splat. Everyone's workstation either grinding, or ground to a halt. Insane and unusual messages on peoples screens left right and centre. Drive mappings all failing.

I discovered what spanning tree was for that day!
__________________
I need a Wiimote. Broken is ok!
fR33z3 is offline   Reply With Quote
Old 12th October 2008, 10:40 AM   #21
Andy_lee
Member
 
Join Date: Jul 2001
Location: Melbourne, Australia
Posts: 209
Default

Here's one:
A small SAN consisting of 6 disk drawers via 2 FC loops to the controllers is having reliability problems. One loop of 3 drawers is fine. The 2nd has a problematic disk drawer which for some reason, can kill off all access to the other 2 drawers in that loop (despite redundant cabling)

We try:
  • Updating all firmwares
  • Reseat & replacing all fiber and SFPs to and from the drawer
  • Reseat & replacing every part in and including the drawer seperately
  • Moving all disks to other drawers
Still we get the same problem.

A power cycle of the SAN gets everything working fine again for a while, but the problem returns after a period of time (ranging from an hour to a week). We try take the drawer out of the loop entirely and problem disappears. Its now been running stable for the last 8 months or so.
Andy_lee is offline   Reply With Quote
Old 12th October 2008, 12:22 PM   #22
brainbug
Member
 
brainbug's Avatar
 
Join Date: Feb 2003
Location: Central Vic
Posts: 195
Default

We have 3 sites connected through a 10mbit, 4mbit and 2mbit pipes. One day connections between all 3 sites were running really slow. We'd had a problem with a couple of switches before so we cycled the power and that did nothing. We spent half a day looking for the source, turns out the 10mbit site was trying to ram XP Sp3 to ~50 computers at the 4mbit site and about 60 at the 2mbit site.

The other guy here neglected to tell me that he added XPSP3 to the list of allowed updates on the WSUS server :P
brainbug is offline   Reply With Quote
Old 12th October 2008, 8:26 PM   #23
Xenon3d
Member
 
Join Date: Jul 2001
Posts: 40
Default

I ran into an interesting issue last Friday :

A client box needed a video card upgrade. I installed the card no problems, turned on the box and have no vga output. Checked the card, did the usual stuff, still no go. I unscrewed the pci slot screws and unplugged a nic and sound card, suddenly its working. I chalk it down to pci cards not playing nice, rearranged them into a config that worked, then screwed them in again. Now the vga stops working. I unscrew the cards, take them back out, all working. I put them back one at a time, all ok. Screw them back in, stops working again.

Eventually figured out that the cheap case chassis was dodgy, screwing the new vga card in was just enough to push the mobo onto the case chassis and short it out. Had me thinking I had gone crazy for awhile.
Xenon3d is offline   Reply With Quote
Old 12th October 2008, 9:49 PM   #24
TonyR
Member
 
Join Date: Jun 2001
Location: NSW South Coast
Posts: 537
Default

This one goes waaaay back.

I worked for a company in England which had installed a new computer room. The mainframe type IBM MVS, SYS370, raised flooring etc.

First day of running , everything went perfectly until 3:30 pm when the system suddenly crashed. Restarted and all was OK.

Next day, same time, give or take a few minutes, down it went.

And the next day

And the next

And the next

etc.


Eventually, they realised that the system crash coincided with the arrival of the tea lady with her trolley and two big urns, one of tea and one of coffee. The fault was traced to a cable trapped under a support for the false floor. The cable was compressed when the trolley ran over it and a short happened bcause the insulation between two strands was slightly damaged. Once the trolley moved on, the cables separated and the system could restart successfully.
TonyR is offline   Reply With Quote
Old 12th October 2008, 9:53 PM   #25
checkers
Member
 
checkers's Avatar
 
Join Date: Jan 2007
Location: Perth
Posts: 613
Default

Quote:
Originally Posted by TonyR View Post
This one goes waaaay back.
Did I read this on Daily WTF recently??
__________________
CCCP
checkers is offline   Reply With Quote
Old 12th October 2008, 11:12 PM   #26
stalin
(Taking a Break)
 
stalin's Avatar
 
Join Date: Jun 2001
Location: On the move
Posts: 4,584
Default

Sounds like you had lovely relaxed computer room entry requirements. Our mainframe (zSeries, with 390 and 370's before that) rooms, and with the 390 and 370 it was rooms didn't let anyone in there without depositing your children as collateral. Thats what an old boss told me.....

Our series 9 MF's today are similar requirements, though now its presenting the old eyeball and thumb.. im sure the next step in security, will be when getting 'intruder lockout' it will cut your thumb off....

anyhoo

For those ultra newbies:

complete S/370 systems




complete s/390 system
stalin is offline   Reply With Quote
Old 12th October 2008, 11:22 PM   #27
PsyKo-Billy
Member
 
PsyKo-Billy's Avatar
 
Join Date: Jan 2002
Location: Townsville
Posts: 2,713
Default

There seems to be an aweful lot of empty space in those rooms...

To get back on topicsomewhat once upon a time as an IBM repair agent IBM insisted on sending us PSUs set to 110V. You only forgot to check a few times. Makes a fair old noise when your head is inches away when you're trying plug the power cable in... It was also fantastic when they started sending them at 230V, before referting sporadically to 110.
PsyKo-Billy is offline   Reply With Quote
Old 12th October 2008, 11:28 PM   #28
Oppressa
Member
 
Oppressa's Avatar
 
Join Date: Jun 2004
Location: Sydney
Posts: 4,903
Default

Quote:
Originally Posted by Iceman View Post
I'm sure there is much worse but the only one that immediately springs to mind was when a vendor once shipped me 15 PC's with identical MAC addresses..
Ahh yes we had the same... about 60 desktops so we had to go around to each one and run an update disc.
__________________
Sydney On Sunday (café review site). 1971 Beetle Resto thread and progress gallery
Main: Cooler Master Elite 342, i7 3930K, Corsair H80, Rampage IV GENE, Corsair 4x4Gb 2133Mhz DDR3 Dominator GT, 5870, OCZ Vertex 3 MAX IOPS 120Gb, 1Tb Western Digital Green, 2 x Pioneer DVR-212
HTPC: Silverstone SST-GD01S-MXR, i3 540, Scythe Big Shuriken, ASRock H55M-GE, 2 x 2Gb DDR3 1333, 7Tb of storage, Pioneer Bluray BDR-206
Oppressa is offline   Reply With Quote
Old 13th October 2008, 10:39 AM   #29
DigitalStill
Member
 
Join Date: Jun 2002
Location: Queensland
Posts: 26
Default

Quote:
Originally Posted by Squeezer View Post
One of our workgroups were conducting a training session and they grabbed a crusty old Switch as there were approx 15 people with PCs laptops int he training session. Someone managed to put a cat5 cable from one port of the switch straight into another port on the switch.

Causes a few problems as the switch further up the rung wasnt configured to stop broadcast storms
Had a similar issue at one of my old jobs at a large retailer, only had about 20 workstations and 1 server, but all the workstations used POS that required TCPIP connectivity to function at all. The building was very large with many many network ports, after replacing the switch and router, finally decided to take a walk around and in an unused office behind a desk was a cat 5 cable coming out of one port in the wall into the port right next to it. Turns out the cleaner had done it while vacuuming!!
__________________
- DigitalStill

"A woman's mind is cleaner than a man's. She changes it more often."
Oliver Herford
DigitalStill is offline   Reply With Quote
Old 13th October 2008, 1:16 PM   #30
TonyR
Member
 
Join Date: Jun 2001
Location: NSW South Coast
Posts: 537
Default

Quote:
Originally Posted by stalin View Post
Sounds like you had lovely relaxed computer room entry requirements. Our mainframe (zSeries, with 390 and 370's before that) rooms, and with the 390 and 370 it was rooms didn't let anyone in there without depositing your children as collateral.
Actually, we had the same stringent requirements, but the outer area was also raised and the cable was trapped very close to the dividing wall, very close to where the trolley was parked after crushing the cable.
TonyR is offline   Reply With Quote
Reply

Bookmarks

Tags
computing, enterprise, epenis, problems, wierd

Sign up for a free OCAU account and this ad will go away!

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT +10. The time now is 3:09 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2013, Jelsoft Enterprises Ltd. -
OCAU is not responsible for the content of individual messages posted by others.
Other content copyright Overclockers Australia.
OCAU is hosted by Internode!