Default is RCD mandatory on GPO?

I had a rather large electrical group in sydney out to install a pair of 20A GPOs (flat pin) in a residential property.

Since they are primarily intended to run some heavy motors, I requested a quote for a pair of D curve breakers and whatever RCD is required to protect the pair of circuits.

Quote was sent with 2x20A circuit installation+MCB/RCD noted, which I signed and returned.

Happy fella turned up to do the installation, and left behind a pair of 20D mcb's and no independant RCD.

Upon razzing head office I was told that no-one makes a combined rcd/mcb in d curve and because i was running machinery I didn't need an rcd.

Now, since this is a flat pin gpo, i also plug my hand tools into the circuits (which is why I wanted GPO's and not round pin specials or hard wired machines) and the decision to ignore the RCD on the quote was not made in consultation with me.

My question at this point, ignoring the poor customer service, is the legallity of having a pair of GPO's with no RCD - is this allowed? My way out of the mess is to back off to a C type RCBO (the circuits are slightly over-rated anyway and the 5-10n is sufficient for the motor start anyway since they are mostly unloaded at start) or to buy a plugin RCD to use with the hand-tools. This still doesn't help me if the presence of the pair of open outlets isn't legal though.
bonox is offline   Reply With Quote

Join OCAU to remove this ad!
Old 3rd May 2011, 10:29 AM   #2
aXis
Member
 
aXis's Avatar
 
Join Date: Jun 2001
Location: Kalgoorlie, WA
Posts: 3,647
Default

Can you keep the D-Curve breaker and get a seperate RCD?

I'd hold them to their quote and ask them to come up with a fair solution.
__________________
Former OCAU Extreme Cooling Club H2O Member
Intel Core Duo E6600 Noctua NH-U12F
aXis is offline   Reply With Quote
Old 3rd May 2011, 10:35 AM   #3
bonox Thread Starter
Member
 
Join Date: Jul 2001
Location: Sydney
Posts: 3,333
Default

i'd like that solution, which is the same pattern as the rest of the house. Will a 20A RCD handle 300A for 10 seconds? Not that it would actually see that, but i guess you need to size it to the rest of the circuit...?


Still don't know if the existing installation contravenes the regulations in nsw though.... thoughts?
bonox is offline   Reply With Quote
Old 3rd May 2011, 11:10 AM   #4
RussellK
Member
 
Join Date: Jun 2003
Posts: 383
Default

Quote:
Originally Posted by bonox View Post
Still don't know if the existing installation contravenes the regulations in nsw though.... thoughts?
I'm pretty sure it does - if it's a new power point circuit, it's gotta have an RCD. If it was fixed wiring to a machine, ie. no plug & socket, then it wouldn't require one.
RussellK is offline   Reply With Quote
Old 3rd May 2011, 3:50 PM   #5
sbadman
Member
 
Join Date: Oct 2006
Posts: 503
Default

20A isn't that heavy, add another zero and you're starting to talk :P

Seriously though, it is irrelevant what you intend to use the GPOs for, they are legally required to have RCD protection. Clipsal's RCD range for example has two and four pole available in 40 and 63A, which indicates their continuous current rating before they melt. There is no rule that says the RCD/MCB must be combined into one unit, but there is certainly one that all GPO's need RCD protection!
sbadman is offline   Reply With Quote
Old 3rd May 2011, 4:19 PM   #6
BlueRaven
Member
 
BlueRaven's Avatar
 
Join Date: Jul 2010
Location: Sydney 2068
Posts: 2,773
Default

Any particular reason why you can't have one round pin/captive outlet + d-curve breaker installed for your plant and a standard GPO + combined RCD/MCB installed for your hand tools?

Not exactly what you wanted, I know, but it just seems heaps easier to me. Plus, even the knobs that quoted you should be able to sort that out, and at a lower price too.
__________________
"Science is more than a body of knowledge, it's a way of thinking, a way of sceptically interrogating the universe with a fine understanding of human fallibility." - Carl Sagan

You can never explain a good pun to a kleptomaniac... he always takes things literally.

Last edited by BlueRaven; 3rd May 2011 at 4:25 PM.
BlueRaven is offline   Reply With Quote
Old 3rd May 2011, 4:20 PM   #7
xc351
Member
 
Join Date: Dec 2005
Posts: 1,282
Default

a normal gpo requires a RCD but being a 20A and well its not a gpo circuit i think it doesnt.

GPO is general power outlet.

same how im 99% sure 15A aircon points don't need a gpo.

i can check my as3000 friday if need be
xc351 is offline   Reply With Quote
Old 3rd May 2011, 4:25 PM   #8
HotHed
Member
 
Join Date: Aug 2004
Location: Melbourne, Australia
Posts: 849
Default

i used to do installs in factories. You can buy GPOs with RCDs built into them, this sounds like your best option. (machines for one gpo, hand tools for seperate gpo with rcd)
HotHed is offline   Reply With Quote
Old 3rd May 2011, 4:30 PM   #9
sbadman
Member
 
Join Date: Oct 2006
Posts: 503
Default

Quote:
Originally Posted by xc351 View Post
a normal gpo requires a RCD but being a 20A and well its not a gpo circuit i think it doesnt.

GPO is general power outlet.

same how im 99% sure 15A aircon points don't need a gpo.

i can check my as3000 friday if need be
No need

Clause 2.6.3.2 Other electrical installations
Additional protection by RCDs with a maximum rated residual current of 30mA shall be provided for final subcircuits sypplying -
(a) socket-outlets having a rated current no exceeding 20A

and 2.6.3.1 doesn't specify a maximum outlet rating at all, so even 15A aircon points need one. Basically, if it's possible for an unqualified person to plug and unplug from it, it needs one. Bear in mind that it's not limited to single phase outlets, 20A 3 phase outlets would be covered under this clause as well.

I'd be betting that the person you spoke to at head office has never even read AS/NZS3000.....

Last edited by sbadman; 3rd May 2011 at 4:35 PM.
sbadman is offline   Reply With Quote
Old 3rd May 2011, 4:31 PM   #10
ArmoureD
Member
 
ArmoureD's Avatar
 
Join Date: Sep 2002
Location: Earth
Posts: 561
Default

As far as I know (since I last checked over a year ago) ALL socket outlets and lighting points are required to be on an RCD protected circuit.

If the new sockets are on new circuits, they MUST be on an RCD.

If the new sockets are attached to an existing non rcd protected circuit, then the circuit MUST have RCD protection installed.

If the sparky swapped a worn/broken socket with a new identical one then they dont have to be on an RCD if an RCD was not originally installed. Although it is highly recommended.
ArmoureD is offline   Reply With Quote
Old 3rd May 2011, 4:40 PM   #11
BAAZMAN
Member
 
BAAZMAN's Avatar
 
Join Date: Jun 2004
Location: melb, 3106
Posts: 902
Default

If it is a fixed piece of machinery and therefore, assuming that it will remain the only piece of equipment used of the 20A outlet, it does not legally require a RCD.

edit: but the outlet needs a label stating that it doesnt have RCD protection and that it is for a dedicated piece of equipment.

That bieng said, you asked for and paid for an RCD and one should have been installed. As previously stated RCD modules can be installed at the GPO, especially easy if a "56 series" weatherproof/captive/industrial outlet has been used.

edit2:
Quote:
Originally Posted by bonox View Post
i also plug my hand tools into the circuits
just re-read OP and as you plan to use portable equipment on said gpo's, it does require a RCD
__________________
I thought i was wrong once, but i was mistaken.
Quote:
Originally Posted by Scott46 View Post
Men don't know a great deal about women yet we still like to ride them
Photo Gear Folding 1.5mil+ pts Check out my Free Porn

Last edited by BAAZMAN; 3rd May 2011 at 9:00 PM.
BAAZMAN is online now   Reply With Quote
Old 3rd May 2011, 8:41 PM   #12
bonox Thread Starter
Member
 
Join Date: Jul 2001
Location: Sydney
Posts: 3,333
Default

Quote:
Originally Posted by <BlueRaven> View Post
Any particular reason why you can't have one round pin/captive outlet + d-curve breaker installed for your plant and a standard GPO + combined RCD/MCB installed for your hand tools?
two machines = two circuits. These two points are intended to cover a pair of 4kW motors, a VFD and a welder. There's a very specific reason I wanted flat pin GPO's. I will only have a pair of machines running together, but they'll get swapped around regularly.

That said, I see no reason why you shouldn't have an rcd on any equipment with a visible and unarmoured flex lead - it may be a 5hp saw, but that doesn't mean you can't damage the lead or get an internal fault that an rcd would pick up without you having to rely on a heavy earth lead to cover until the breaker blows.

Especially when the breaker will let you put 300A through the circuit for a reasonable amount of time, it becomes a little about fire risk mitigation as well as personal safety.

Old mate in charge of the job said he'd try to find a solution a couple of weeks ago - time to remind him I think....

Thanks all for the AS feedback. Makes it even easier to argue for what I requested if the install is illegal.

Last edited by bonox; 3rd May 2011 at 8:44 PM.
bonox is offline   Reply With Quote
Old 3rd May 2011, 9:52 PM   #13
Nick_Henchel
Member
 
Nick_Henchel's Avatar
 
Join Date: Dec 2005
Posts: 246
Default

Quote:
Originally Posted by sbadman View Post
No need

Clause 2.6.3.2 Other electrical installations
Additional protection by RCDs with a maximum rated residual current of 30mA shall be provided for final subcircuits sypplying -
(a) socket-outlets having a rated current no exceeding 20A

and 2.6.3.1 doesn't specify a maximum outlet rating at all, so even 15A aircon points need one. Basically, if it's possible for an unqualified person to plug and unplug from it, it needs one. Bear in mind that it's not limited to single phase outlets, 20A 3 phase outlets would be covered under this clause as well.

I'd be betting that the person you spoke to at head office has never even read AS/NZS3000.....
Spot on. I was waiting for someone to bring this up. As stated a socket outlet (whether it be single or 3 phase) with a rated current of more than 20A doesnt need to be on a RCD by the regs.

Saying that, if it were a residential premises where this socket outlet was being used to supply power to different appliances, i would probably still whack it on an rcd.

Out of interest what the FLC of the motors you plan on running??

Cheers, Nick.
__________________
i5 2500K @4.2Ghz, Z68 Extreme3 Gen3, 8gb Kingston HyperX, OCZ Vertex3 60gb, Seagate 2tb, BenQ GL2440
Nick_Henchel is offline   Reply With Quote
Old 3rd May 2011, 10:52 PM   #14
TERRA Operative
Member
 
TERRA Operative's Avatar
 
Join Date: Jul 2005
Location: Niraikanai
Posts: 6,907
Default

Quote:
Originally Posted by BAAZMAN View Post
If it is a fixed piece of machinery and therefore, assuming that it will remain the only piece of equipment used of the 20A outlet, it does not legally require a RCD.
When the AS3000 refers to fixed machinery (Clause 1.4.6 to 1.4.10), I think you'll find it makes no difference to the requirement of an RCD if it is connected to the supply via a socket outlet. (refer clause 4.3.1 to 4.3.4,

If the machinery is bolted down, but you can still unplug it, the circuit requires an RCD as indicated by clause 2.6.3.1 and 2.6.3.2 as posted previously.

There is no provision for a fixed appliance (1.4.7) not requiring an RCD if it is on a socket outlet.

In fact, clause 2.6.3.1 (c) states that an RCD is required for "directly connected hand-held electrical equipment, e.g. directly connected hair dryers or tools;" when installed in residential, domestic or common areas.

Clause 2.6.3.2 (c) reiterates the RCD being required for direct connected tools.




Can people please stop inventing hearsay about these things? It's ignorant, stupid and just plain dangerous.
TERRA Operative is offline   Reply With Quote
Old 4th May 2011, 1:08 AM   #15
2xCPU
Member
 
Join Date: Jan 2005
Location: melb
Posts: 2,830
Default

Quote:
Originally Posted by TERRA Operative View Post
Can people please stop inventing hearsay about these things? It's ignorant, stupid and just plain dangerous.
Especially after the correct info has been posted.

2.
__________________
If "building a computer" doesn't involve powertools, you're just assembling spare parts.
----
The universe is made up of atoms and empty space, the rest is mere opinion. Democritus, 400 BC.
2xCPU is offline   Reply With Quote
Reply

Bookmarks

Sign up for a free OCAU account and this ad will go away!

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT +10. The time now is 9:49 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd. -
OCAU is not responsible for the content of individual messages posted by others.
Other content copyright Overclockers Australia.
OCAU is hosted by Internode!